What are the general practice and standards for electrical equipment installed in the Hazardous Areas?

Asked by cuchiang 5 years, 3 months ago | 1 Answers


1 Answer

1
dperri 5 years, 3 months ago

The following installation practice should be used:

  • Drilling of entries in EEx d enclosures is not permitted.
  • EEx stopping plug of an approved type should be fitted to all unused entries of EEx equipment.
  • Only EEx d/e glands should be used with EEx enclosures.
  • Only tools suitable for EEx equipment should be used.
  • Approved non-setting compound (MolykoteTM) on flame paths of EEx equipment should be applied as per manufacture’s standard and when flame paths are not protected against corrosion.
  • Painting of the flame paths is not permitted.
  • There shallshould be no obstruction around the flanges of EEx d enclosures.
  • Cutting, drilling or welding hazardous area equipment is not permitted, unless by certified personnel.
  • Any alteration to certified equipment which may invalidate the certification should be avoided.
  • Contractor should record all details of Contractor supplied equipment on the ‘hazardous area equipment certificate list’. Electronic template will be issued by owner company.

Related Posts


Consideration in selecting fused switches in a MCC
Consideration in selecting fused switches in a MCC

This article provides recommendations on fused switches in a MCC for short circuit protection of motor and feeder branch circuits.The …

Electric Heat Trace Systems Maintenance
Electric Heat Trace Systems Maintenance

Recommendations:IEEE-515, Standard for the Testing, Design, Installation, and Maintenance of Electrical Resistance Trace Heating for Industrial Applications, Section 8.4."Periodic operational …

Positive isolation philosophy
Positive isolation philosophy

What is Positive Isolation?Positive isolation is a method to totally isolate equipment or a section of the plant from a …

Unauthorized changes to alarm configuration should be checked as part of circuit maintenance
Unauthorized changes to alarm configuration should be checked as part of circuit maintenance

This following case supports the need to provide a permanent record to document controller settings/configuration for programmable heating controllers in …