Purging system time delay to produce an alarm or shutdown?

Asked by karthikrg 6 years ago | 2 Answers

I am looking at putting together a purging system intended to produce an alarm or shutdown action. What would be the typical industry practice of the time delay before an alarm or shutdown needs to occur?


2 Answers

0
franchaze 6 years ago

I should also add the followings:

  • Purging system should include overpressure relief
  • If purge and positive pressure ventilation system is used, the system should be designed, fabricated, and installed per ISA S12.4
  • The flowmeters located in areas classified as hazardous shall be certified for installation in the area by UL, FM or other industry accepted authority

0
franchaze 6 years ago
The purging system intended to produce an alarm or shutdown action should incorporate a 0-30 second adjustable time delay before alarm or shutdown. An initial setting should be 30 seconds.