Minimum distance between LV cables and all other cables within electrical installations on a FPSO?

Asked by Dan01 5 years, 11 months ago | 1 Answers

What is the typical minimum distance between LV cables and all other cables within electrical installations on a FPSO?


1 Answer

0
wangroc 5 years, 11 months ago
Consider a minimum distance of 150 mm between LV cables and all other cables for confined spaces such as the engine room, accommodations, etc. Spacing between LV cables and all other cables in non-confined spaces shall be maintained at 300 mm. If all confined spaces are maintained at 300 mm, it will have a cost impact (increase).