Extent of Fire Area?

Asked by brysenlin 3 years, 5 months ago | 1 Answers

What is the recommended fire area when designing and placing equipment in a facility? In another word, when planning the general layout of a facility, what should be considered?


1 Answer

0
wangroc 3 years, 5 months ago

Per API RP 521, if the equipment is located in an area where type and volume of the inventory and drainage system design is such that a sizable fire might occur:

The horizontal extent of fire zone should be a 65 ft diameter circle from a potential source of fire.  A shorter fire zone could be assumed if equipment is segregated by firewalls or by a curbed area capable of containing or restricting the exposure to the spilled inventory.

Assume that all piping and equipment up to 25 ft above deck, ground, or any other fire-supporting surface is exposed to fire.

For air coolers with tubes located higher than 25 ft above grade or other surface at which a major fire could be sustained, the extent of fire should be as follows:

  • For forced draft units (the tubes would be shielded from radiant heat exposure by the fan hood), wetted area should be taken as zero (no fire exposure).
  • For induced draft units, the wetted area should be taken as the projected area (length multiply width) of the tube bundle.